S800 I/O - DI830, DI831 flashing red fault LED
Problem:Solution
- The problem is solved by a firmware change
The firmware has been changed to get a more robust handling of the fault LED. The new firmware is included in PR:F and PR:G of the hardware units concerned.
[ref 3BSE033353 VASMASOITA0856 ]
- S800 I/O - DI830, DI831 flashing red fault LED
Due to component tolerances an internal timing problem can occur. This results in a flashing red fault LED. We have not observed any other disturbances of the function connected to the flashing red fault LED.
Product concerned
S800 I/O
Hardware concerned
DI830, DI831 PR: A, PR: B, PR: C, PR: D, PR: E
- Article imported from the previous version of KnowledgeBank
Add new comment