DigiVis is not updated – CN 37-085 EN
Problem:Solution
- Shut down and restart DigiVis after frequent reconfigurations
Everything works fine once DigiVis is restarted.
However, the problem will recur after a further 25 downloads.
Ensure that DigiVis is shut down and restarted after frequent reconfigurations.
The problem is corrected in Service Pack V5.2SP2, V6.1SP4 andV6.2SP1.
The Service Packs V5.2SP2 and V6.1SP4 are available in ABB internet under
www4.abb.de/downloads/freelance.
Service Pack V6.2SP1 will be released in the next time.
- Operation and Observation
In DigiVis values are not displayed with their current validity if DigiVis has been reconfigured approx. 25 times.
The display is not updated despite changes to the values, the version error is not recognized and the writing procedure is not checked. In DigiVis an internal timer ID is lost.