Module CEB 10 - Invalid alternate value EW=1 for module BAUS-I
Problem:Solution
- Where EW=0 the outputs remain highly resistive (L potential).
- Automation
After cold starting, loading or parameter setting on the module CEB 10, the input buffer memories that are read from the module BAUS-I for the direct output are incorrectly set to 'invalid', even though a valid H/L signal is present at the input.
Where EW=1 this initialization can lead to an undesired H signal on the allocated binary output.
This effect only occurs when the parameters UMS_EW and EW are set to 1 and a valid 0 signal is recognized at the input during the start phase.
- Incorrect initialization of the input buffer memories used by the BAUS-I with the invalid code
- Article imported from the previous version of KnowledgeBank