Graphic Editor - BIA module defective
Problem:Solution
- Reconfigure the BIA module
The BIA module for outputting a binary value has the parameters 'Festwert' and 'E_Wert' for the handling of alternate values. In this module the function does not correspond to the designation of the parameters.
The parameter designated with 'E_Wert' on the graphic symbol is the parameter at which the switch-over between the current value and the alternate value takes place.
The parameter on the graphic symbol with the name 'Festwert' allows adjustment of the alternate value (L-level/H-level).
In order to ensure the correct handling of alternate values, the BIA module must be reconfigured. Errors do not occur only when the parameters 'Festwert' and 'E_Wert' are both configured with the same values.
If an update has meanwhile been carried out in the system, the BIA module can be brought up to the correct status with the key combination ^GD (insert default data for configuration data).
- Note the configured data and check whether they are correct. Move the cursor to the 'Festwert' input and type ^GD. If necessary, change the default value. Proceed in the same manner for the 'E_Wert' input.
- Service Station
The parameter designation 'Festwert' and 'E_Wert' of the BIA module is exchanged.
- Exchange of the parameter for the handling of alternate values
If the parameters are switched, incorrect handling of the alternate values may result.
- Article imported from the previous version of KnowledgeBank