Problem:Solution
- OS1.6/1p1 Patch may fail to load
The user will see an error in the /var/adm/sw/swinstall.log file which looks like: ERROR: 'hostname:/': One or more filesystems that appear in the filesystem table are not mounted and cannot be mounted.This has been seen on a couple of occassions in both the QA Lab and the Columbus Staging Center. I believe this is occurring because people are loading their OS1.6/1 Operator Stations with a local CD ROM drive. Prior to loading the patch, the CD ROM drive has been removed physically from that machine. They then attempt to load Patch 1 using the remote swinstall capabilities. To get around this problem, use the following command instead of the published one on page 3-2 of the AdvaCommand Version 1.6/1 Patch 1 Release Notes: swinstall -x mount_all_filesystems=false -s
- OS1.6/1p1 Patch may fail to load
When loading OS1.6/1p1, the installation may fail during the initial swinstall command.
- Article imported from the previous version of KnowledgeBank
Answers
Cause: Article was imported from the previous version of KnowledgeBank Resolution: