Ghost Node Removal on MasterBus 300 Advant Stations
Problem:If a node is removed from the masterbus 300 network, it will be reported as a fault on the other operator stations. This will give a red indication on the status page for all nodes.Symptoms:
- How to remove ghost nodes from Advant Operator stationsGhost node needs removed from the system status and overview page
Answers
Cause: Ghost node causes fault indication on status page Resolution:
Open the RTA config window. When the window is fully opened and the asterix is displayed, type and enter the command
" LOCPSET CMDS:TP01.CT "
When the command set is loaded, type in
" OMVT " (This stands for open master view table)
This will give you three choices.
1. List
2. Add
3. Remove
First, list the nodes. Find the node you want to remove.
Then select "remove". When asked which node, type in the node you want to remove.
Do a " TSESS" to terminate the session and then restart the node.
This procedure must be done on all nodes on the network to remove the ghost node from being displayed.