The process of importing a tag list from a DCU into 800xA crashed
Problem:The customer was no longer able to import a tag list exported from a DCU using Composer CTK after a 800xA 5.0 FP4 upgrade. An error occurred during the failed tag list import into 800xa which read "Cannot initialize the object 1MSET6 (no or incorrect Control Connection Aspect found) during DCI tag import".Symptoms:
- Message "Cannot initialize the object 1MSET6 (no or incorrect Control Connection Aspect found) during DCI tag importThe process of importing a tag list from a DCU into 800xA crashed
Answers
Cause: The issue is caused by failing to comply with the mandatory installation sequence of the upgrade of the 800xA for DCI Software from 5.0 SP2 to 5.1. Resolution:
When upgrading an 800xA system that includes both 800xA for DCI and 800xA for Batch the installation sequence described in for following section of the 800xA installation manual must be followed or the installation of the 800xA for DCI software will erase the Batch object form the 800xA system. The missing Batch objects will cause the Tag Import process to fail with the error previously described.
If you have this issue on a system you must follow the procedure below to correct the issue.