Event from InformIT History about message log not being configured
Problem:IM generates 800xA events every two minutes if either the PDLMSGLOG or the IMMSGLOG is not configured on the IM. Some customers do not need either of these two event logs configured and consider the frequent events a nuisance.Symptoms:
- IM generates event every 2 minutes if either IMMSGLOG or PDLMSGLOG is not configuredhsEventLogCollector - PDLMSGLOG_ww_xx_yy_zz is not configured.
Answers
Cause: Not configuring either a PDLMSGLOG or an IMMSGLOG. Resolution:
There are two registry settings that will suspend the creation of either event. Use REGEDIT to set the desired keys to 0 to suppress either or both of the events.
HKEY_LOCAL_MACHINE\SOFTWARE\ABB\History\EventLogCollector\GenerateMsgLogEvent
HKEY_LOCAL_MACHINE\SOFTWARE\ABB\History\EventLogCollector\GeneratePDLMsgLogEven
t
After setting the registry entry you must restart the IM using the PAS for the new settings to take effect.