Full Maintenance Backup Fails with Error (Unable to save file, 0x80004005)
When executing a full Maintenance Structure backup of the aspect system, you may see an error similar to the following:
Mon Jun 14 13:37:50 2010 D:\BACKUP\System Configuration Structure
Backups; 2010-06-14; 13-37\Aspect System Structure0.afw created
Mon Jun 14 13:37:59 2010 D:\BACKUP\System Configuration Structure
Backups; 2010-06-14; 13-37\Graphics Structure0.afw created
Mon Jun 14 13:40:33 2010 Unable to save file D:\BACKUP\System
Configuration Structure Backups; 2010-06-14; 13-37\Object Type
Structure0.afw 0x80004005
Mon Jun 14 13:40:33 2010 Unable to save file D:\BACKUP\System
Configuration Structure Backups; 2010-06-14; 13-37\Object Type
Structure0.afw 0x80004005
- Error 0x80004005 when running backupErrors in full maintenance backup
Answers
Most of the time, when the "unable to save file" error appears, it relates to inadequate disk space on the disk to which the backups are being saved.
However, it is important to note that before the file is written to the final location (partition), it must be temporarily written to the system drive (C in most cases). For example, let's assume the file Object Type Structure0.afw listed in the error above has a final size of 850mb. You've checked the D partition (where the backup is being saved), and see that there are 20GB free. However, the C partition has only 500MB free. The backup service will be unable to temporarily save (serialize) this entire file to the C partition before writing it to D, and the error 0x80004005 results.