Faceplate shows a triangle with a question mark in it.
Problem:
Note: Question mark in first Faceplate Triangle due to illegal character in Tag Name
or a Duplicate Tag name in 2nd FaceplateSymptoms:
- Faceplates have triangle with a question mark in it.With question question mark in Faceplate triangle, masks off alarm indication, border around triangle should blink when tag is in alarm
Answers
Cause: Question Marks in the Faceplate triangle means there is an alarm configuration error. Typical causes are spaces (or other illegal characters) in the CondName or CondNameDiff parameter, or the parameter is blank (which happens by default when Control Modules are copied and pasted; the system blanks them out as not to create duplicates). Duplicate Tag Names in the 800xA System will also cause the Question Mark Triangle on Faceplates
Resolution:
Resolution:
Making Tag Names uniques in 800xASystem, or removing spaces or illegal characters in the CondName & CondNameDiff parameters corrects this problem