Failed to create Generic OPC Server Network
I tried to create a "Generic OPC Server Network" in the Control Structure (Root). I can select my 3th party OPC Server. But when i click ok there is the following fault:
Failed to create the object.
E_AFW_AOM_OBJECT_NOT_FOUND(0x8abb090a) Object not found in the object manager.
Seems that there is something missing.
PLC Connect extension is istalled
800xA 5.1 FP4
Answers
Hmm... odd.
Please run an "afwsct" on the Control Structure and check if there is some damaged structure references there. Such can cause arbitrary problems.
C:\>afwsct -s "Control Structure"
Checking structure 'Control Structure'
SCT succeeded
If you get an error message, please contact your regional ABB support center for further advice. Turning on the "repair" flag should be done with caution and assistance from support. Some problems can't be repaired with this tool, or possibly goes worse...