can ch1 of AI 810 is configure as four wire while ch2 configure as two wire?
AI 810
Answers
Hello,
Yes you can combine two and four wire in the same module ensure power supply is provided for mtu to work for 2 wire.
2 wire for mtu tu830 B and C terminals
4 wire for mtu tu830 C and A terminals.
Refer mtu with ai810 for connection in manual
Add new comment