Log Configuration: Read Quality 'Bad, Not Connected' after replacing control module type
I replaced a control module with a new type in the control builder. The new type has the same variables to log (same name). After download to controller, the variables to log appears on the aspect 'Control Module' register 'Property View' with the correct value. But in the aspect 'log configuration' is the read quality always 'Bad, Not Connected' and the value '0.000'.
A new instance of the new control module type (With no replacing) works.
In the Basic History storage location exist the files.
How can I bring the logging to work?
Answers
Hello,
If you rename a block name then you have to reconfigure the log aspect the existing log aspect referring to older blocks check the name and check the history source configured and running
After the redundant Basic History services restarting, the logging works. But always after a replacing to restart the basic history services is not the comfortable way.