Is there the potential in 800x system to Save all kinds of alarms even confirmed, deleted from the list or etc
Hi,
if the system has this potential, is it possible to access and refer to saved alarms?
Where is the configuration place of this capability
How to change the capacity of saved data(Alarms)?
Answers
Hello,
All alarms can be an event but not vice versa so deleted alarm u can find in the event list but u can't find in alarm list so saving the all event list by copy paste r use the data direct AE tool to browse n append.
Note: if you have IM/history configured then you can get as max equal to may 1lacs in general if IM not used you can get may around 10000 in max after that fifo
Hello,
you can copy directly from event list, and paste in another tool,
or use DataDirect if you like Excel.
If you like SQL you have SQL-table to SELECT from if you have an IM.
You can define "Number of alarms in main storage" (default 10000) in Service Structure, Alarm Manager, Basic Service Group. Special Configuration tab on Aspect Service Group Definition.
/Ronny
Add new comment