License error for System 800XA for advant master
This is regarding the License error "Remote applications are running wihtout valid licenses" appearing in all workstations.
Please find the attachment with the error "violation count 5451" for "TAG_RED"
Let me know if there is any work around to avoid this license error popup,
What is the relationship beatween "Remote applications are running without valid licenses" and "violation count 5451" TAG_RED
Answers
Each object outside the Object Type Structure having one or more faceplates will require one (1) TAG.
Objects with more than one insertion point, e.g. Control Structure + Functional Structure will still only drain one (1) TAG.
Hence, multiple faceplate aspects and/or multiple insertion points per object does not increase TAG count. One object = max one TAG will be drained.
If the system has one or more redundant services (a service group with MORE than one service provider) RED_TAGS is required instead of TAGS.
An oddball: a default setup system with 1 AS + 1 CS will need RED_TAGS until the AfwTime Service has been reduced to run in just one of the servers, normally the CS.
So, if your system is redundant you have more objects with faceplates than TAGS_RED seats in the CLS. Buy a bigger license, or remove objects with faceplates until the system fits within your existing license.
On the other hand, if your system is not redundant, one or more service groups has been configured with more than one service provider. Reduce the groups to one service provider only and the system will fall back on requiring regular TAGS.
by admin Rank: 44 on 1/19/2016 5:42:07 PM | Like (0) | Report
Hello,
Please note that this not an official supportline portal. For that get connect with your local ABB people.
-/Admin
Add new comment