Hi,
I am A newbie Coder Working In engineering Station ES100 (AC450 For OS520 ).
I have a difficulty when i try to understand (Read) Program Part (Pc) Like :
StUpCtrl = START UP CONTROL ?
OF = OFF
GtSeq_CON = GT SEQUENCE COMMAND ON
GtTrp23_AC = GT TRIP 2oo3 ACTIVE
CJP00EA001 = CONTROL FUNCTION GROUP STEP 001
As you see this is a simple Abbr so what about :
FuelCtrl_CRS ?
StUpCtrl_HI
CVIgnStk_AC ...ect
if there is any source or guide could help me ?
2) also do you have guys a definition (Programming Terms) for the :
Interactive
interlock
block alarm
fault_Sum
thank you for your time, Kind Regards.
Voted best answer
What You have listed looks like PC element terminal descriptions. These are not standardized but every programmer comes up with his/her own. They are limited in length to 20 characters (or 22 depending on if they are enclosed in "()" or not) which is why you will see a lot of abbreviations. If your system is part of a canned solution from some particular ABB Business Unit, they may be standard for that product, but otherwise you need to get hold of the original programmer, or you are on your own.