800xA SV5.1FP4 Tabbed Workplace Size of pulldown menu
Hi,
currently I am configuring a tabbed workplace. Due to the screen size it is planned using pulldown menus.
My problem is I cannot adjust the length of the pulldown field. The tabs are min 150 / max 300 but the pulldown remains the same size and the display names are cut. The tool tip text size is much to small for an operator.
Is there a chance to change the length of pulldown field ?
TAB: AREA1
Pulldown:
31 Tempera... (31 Temperature Motor 1)
32 Tempera... (32 Temperature Motor 2)
Thanks and regards,
Detlev
Voted best answer
Hello,
The problem related to this is gets corrected in Base System 800xA 5.1 FP4 revD Ru2 so it needs ur system to be updated.
Refer the snap attached for your ref.