AC450 communication with S100 I/O rack
Dear all:
We got a communication problem between AC450 and S100 I/O rack. During test, the power supply for the I/O Rack DSRF197 with DSBC176 was fault, after that, DSBC176 INHIB LED on.
We tested the DSBC176 on other Rack, it’s OK, so we think the problem maybe come from DSRF197, or we can reset this “INHIB” by any method?
Thanks in advance.
BR/Baogen
We got a communication problem between AC450 and S100 I/O rack. During test, the power supply for the I/O Rack DSRF197 with DSBC176 was fault, after that, DSBC176 INHIB LED on.
We tested the DSBC176 on other Rack, it’s OK, so we think the problem maybe come from DSRF197, or we can reset this “INHIB” by any method?
Thanks in advance.
BR/Baogen
Answers
As you can see in the S100 manual the blocking signal comes from within the system.
PBC = backplane bus.
Regards,
Detlev
Add new comment