How is the tag license for MSI works.
We are 8 800xa system each having 1500 tags communicating to main 800XA server using MSI featur.
Do we need to order 1500*8 Tags license on top of 8 MSI license ?
How the tag licensing is calculated ?
Answers
Hello,
It´s depening on which version of 800xA you are running.
On versions before V5.1 FP4 the licensing modell is totaly crazy, you need item no 3BSE061237R1 with a list price in Europe nearby 25000 euro/system you want to connect in subscriber system.
From V5.1 FP4 and towards you only need multisystem tags, redundant or not depening on redundant RAC servers.
Item no 3BSE072204R1 for 100 Multisystem Subscriber tags and item no 3BSE072204R2 for 1000 Multisystem Subsriber tags.
Item no 3BSE072205R1 for 100 Multisystem Subscriber redundant tags and item no 3BSE072205R2 for 1000 Multisystem Subscriber redundant tags.
The subscriber counts tags from each uploaded system so you will need 8*1500 tags in subscriber system if version 5.1 FP4 or later.
Good luck with you 800xA systems!
Best Regards // Mattias