Asset viewer Aspect does not show the status (in color)of the instrument connected.
System Details
800xA 5.1 RevD FP4 used,
Asset viewer Aspect does not show the status of the instrument connected.
* The Asset monitor aspect shows the status "good"
* Control connection shows goood.
but, the actual instrument status color in not getting indicated.
Answers
What is the asset type?
Can you attach some pictures of the Asset Monitor Viewer, suspect graphics (runtime+design), Control Connection aspect (with live data enabled), etc?
It will be really good if you ellobrate your issue , in terms of what indication is coming for Asset monitor is the condition is good and if the condition is alarm state .
However following things you can verify in your system :
1. Verify that Asset tree service is running in Service structure.
2. Verify that Under Aspect System Structure >>Asset Tree , Aspect system >> Asset Viewer , Aspect type >> Asset Viewer , Aspect category -- Icon setting general property aspect check value for UseNamur property is True . if it is False change is to true and verify that Asset Viewer is showing proper indication or not .
If after above two steps your issue is not resolved , probably require more data as mentioned for giving resolution for the problem.
Thanks.