Regarding %MW address problem in AC500
Hello,
I Am using PM573ETH CPU for my new project. In this it will accept %MW0.0...., %MW1.0...., I need to configure for %MW2.0.... to %MW5.0.....
This requirement is for HMI modbus communication. Pls guide me how to do this. When i used AC31GRAF i have not faced this problem.
Regards
Raju
Answers
%MW0.0 = Modbus address 0 (dec)
%MW0.1 = Modbus address 1 (dec)
%MW0.2 = Modbus address 2 (dec)
%MW0.3 = Modbus address 3 (dec)
...
%MW0.32767 = Modbus address 32767 (dec)
%MW1.0 = Modbus address 32768 (dec)
%MW1.1 = Modbus address 32769 (dec) ...
Please read help in ControlBuilder, type Modbus addresses
by rajshasthri Rank: 1000 on 12/30/2015 6:41:16 AM | Like (0) | Report
In our company one of the machine have PM571 CPU. During erection time they have provided program backup. Am trying to check with TK503 programming cable, but problem is communication error. Guide me how to solve this. I need to take program copy from existing PM571 CPU.
Add new comment