Cable to connect with CI853
Hi MMM,
What is cable to connect between slave and CI853. If I use the modbus slave siulator on Computer, could I use TK212A to connect with CI853.
I have tried but it seems that cannot. Always error -4929 (timeout, no answer from slave)
Thank you.
Tuan
Voted best answer
You can use TK212A which is a crossed cable (TX to RX) or a TK853 which is straight cabel (TX to TX). As you go to the computer you need a cross so TK212A should work.
Answers
The TK212A cable should work.
CI853, RJ45:
3=TD (transmit)
6=RD (receive)
See attached document
Add new comment