ip configuration on ac900f
Dear Sir,
COuld you please advise some document on how to configure the ethernet comunication for the first time with ac900f .
Thanks
Voted best answer
Hi geoker7,
If You don't have a way to connect to diagnostic port (serial) than maybe You have AC 900F display unit (TD 951F)? If You have it, then simply restart the controller and push ESC key for a few seconds when it's restarting. You will get into Boot Configuration mode. From there push F1 (to choose IP Address options) and from ths menu You can enable, set the addresses and functions for all 4 ethernet ports of AC 900F.
After You've done just push ESC to go back to the first menu and ESC again to return to booting the controller.
Hope this helps,
Mike
Source: 2PAA109295 M&I – AC 900F Controller manual
Answers
1.Connect Serial cable between AC900F controller and PC
2.Open Hyperterminal/Teraterm(for windows 7 OS) and power off controller
3."PFail" will update in Hyperterminal/Teraterm window if cable is connected properly
4.Power ON controller, data will start updating and keep on pressing "SPACE" bar key till you get "<C>hange, <S>ave, <B>ooting......"
5.press "C" to change the settings, Select [0] will come under "ETH Link Configuration" and press enter
6.Enter your IP address like 10.0.22.xx and press enter
7.Enter your Subnetmask like 255.255.255.0 and press enter till you get "<C>hange, <S>ave, <B>ooting......"
8.Press "S" to save your settings/configuration and press "B" for booting the controller.
Hope that helps.
Best Regards,
Rachit
Dear Rachid.
Thank you.
Actually I dont have serial port .
Is there a way I can do it from the cpu itself? Or via ethernet?
Thanks