connection of 800xA Operator Workplace to a MasterBus 300 control network with Safeguard Controllers
on my job exist ABB Advant OCS with Master Software.Implemented migration from Advacommand 1.7 for windows NT to System 800xA
Now exist 2 Redundant Combined Aspect and Connectivity Server. The Servers Connect to MB300 Control Network via PU410 RTA Unit.
A Problem is Operator Workplaces can not Connect to Dual Safeguard Controllers.(Safeguard Controllers is AC410). Operator can not send any command same as Start/Stop , On/Off, Inhibit, Block, etc... to Safeguard Controllers.
Please Some body Help me That can Solve this Problem.
Answers
Hi Hereby some suggestions for you to check: 1) "ABB 800xA for Safeguard" System Extension must be installed and loaded. 2) Safeguard node(s) defined in Control Structure as type "SG 400 Dual System". 3) "Safeguard Dual Configuration" aspect configured with "virtual Node Number",
see example below with Virtual Node Number = 202 4) 2 pcs NODE_DESCR database elements per Safeguard node, created and configured in RTA board database on Connectivity Server, see example below with Virtual Node Number = 202.
I hope that above will help you.
BR Carsten
VIR_NODE = 202
see example below with Virtual Node Number = 202 4) 2 pcs NODE_DESCR database elements per Safeguard node, created and configured in RTA board database on Connectivity Server, see example below with Virtual Node Number = 202.
I hope that above will help you.
BR Carsten

VIR_NODE = 202

Add new comment