How can i block signal force in SignalinRealM Control Module
Hi,
I want to block signal force for analog inputs for operators also engineering users can be force signal. I use standart control module SignalinRealM. Is it possible to do this adjustment?
Voted best answer
In my reference system, the forcing OPC property require "Operate" permission.
I.e. most operators will be able to force IO.
If library default is not appropriate for your application you can use Property Attribute Override aspects to raise the permission so that regular operator can not write to the .Forced property.
Page 106 in System 800xA Control AC 800M Configuration, 3BSE035980-510.
Pages 54-60 in System 800xA Administration and Security, 3BSE037410-510
/Stefan