K-TEK AT100 Transducer block in Out of Service
Hello,
I am using K-TEK AT100 FF Transmitter, Assigned and downloaded the configuration but the transducer block is in Out of Service mode, how to make it to auto mode. If there are any specific settings kindly help for the same.
I have not seen any device transducer block in out of service by default.
Let us know is there any issue with the sensor value status bad?
Answers
Hello,
Ensure that proper CF is loaded and check the sensor type is selected with primary or secondary variables and check.
Check the device type, revision no are matching with actual device through resource block
Perform device, h1,ld level download by looking at the block down arrow mark.
Then perform project plausibility check and do the opc reconcile
Hi Narender,
Please make sure you dont have any block error in the TB block. Incase if you have any error you need to fix the same. The other cause could be mismatch of the unit and the channel of the particular AI block. If you match the same the block error may be removed. Please confirm you dont have any error in the TB block and it is still showing as out of service?
jothi
Add new comment