How can I connect a 4wire 4-20ma transmitter with AI810 module on MTU TU810V1
Self explanatory
Answers
In the attached document you can see that.
in the example Ch 6 is 4-20mA, 4 wire transmitter.
The output of the 4 wire transmitter you have to connect as follows:
+ to B6 (or B1, or B2, or B3... for Ch. 1, 2,3 ..)
- to A6 (or A1, A2, A3... for Ch. 1, 2,3 ..) which is ZP or L- or 0VDC of the module
Source: 3BSE020924-510
Refer the attached connection diagram (channel 6) for connecting 4 wire transmitter using AI810 with TU810.
Add new comment