Function Designer, Diagram
Hi,
we used 800xA 5.1 with Revision B.
We start to create our Typicals with the diagrams in 800xA.
For the Analogue Input we used SignalInRealM, and we want to set the Limit Values
in the Diagramm.
LevelHHH will be set with a fixed value and the other will get an iniatial value which can be change after initialization.
When we set the limit value direct to the Interaction.Par the we get the message
"At least one endpoint of a data connection must be a block with a data flow order value.
If we create a CM, inside we set an fixed value to an output and connect the output from the cm to the Interactioon Par-> then it is working.
This function was not the same as before.
Answers
From SV 5.1 with the diagram concept there has been changes in the way the code is handled in CBM for applications created in Function diagrams.
In your case connect a move block to the terminal LevelHHH of the interaction parameter and then feed the initial vaue to the move block.
by Prashanth Rank: 61 on 5/17/2013 3:31:13 AM | Like (0) | Report
can you provide a picture if the workflow that you are following? It will help us understand better