Hart communication error
Hello.
I added 1 Hart device of Rose Mount Press Transmitter.
And completed configuration of Hart communication.
1. Hart DTM in IO Ch.
2. Testing for the Force in actual transmitter to 800xA System in used to Hart function
3. Display the faceplate communication is no problem.
4. Control connection of Hart parameters.(Quility is problem)
-> I can not find the problem.
Date Set is valid.
My system ver. : 800xA 5.1 FP4.
Thank you.
Answers
Probably you did not do the P/H OPC server configuration. Run OPC server configurationby reserving and right clicking on Device in Fieldbus Management aspect.
Also you need to setup services for P/H OPC server in service structure.
Hello,
For Hart to work ensure tool routing is enabled and downloaded for the controller and device assigned to the channel thrrough device management