Faceplate for PID in compact HMI
In 800XA faceplate for PID is automatically asigned when we create one PID instance,
But in compact HMI how is it possible to assign one faceplate to one PID controller of ABB libarary?
Voted best answer
Hello,
As Compact HMI has PLC Connect features which has very limited options as Stefan Said.
You can create your own PID Faceplate i have created though which works very well.
If you are using MConnect which as default faceplate you can acess it.
Answers
- System 800xA comes with AC 800M Connect and full object type and graphics packages
- Compact HMI comes with PLC Connect and a reduced set of types and ready made graphics
If the PLCC ready made graphics does not fit, you must build your own or import from some source.
Add new comment