Hi I am using PM865 HI controller,when I try to download the program.
it reaches to sending domain step then controller tends to go in fault mode each time.
for ref pl find attached controller log.
it reaches to sending domain step then controller tends to go in fault mode each time.
for ref pl find attached controller log.
Answers
No memory dump due to missing compact flash card.Please insert a compact flash card and capture the dump files and contact the local supportline for dump analysis.
Problem seems to be in your SM810 module. "No SM810 found for HI controller!"
Rest of the mesages are all a consequence of the above.
Can you check the status of SM810 before download and ensure both SM810 are OK.