How to reset fault of ABB acs800 by parameters?
I have a software that control drive by EFB .
I'm looking for parameter that by change value of it fault of drive reseted.
Please guid me.
I'm looking for parameter that by change value of it fault of drive reseted.
Please guid me.
Answers
Hi
To reset from external command the drive, I suggest you carefully read the FW manual and in particular the instructions of the parameter group 16.04, where you will find the reset modes indicated both in HW - for example with a digital input - or via fieldbus.
BR
Flavio
To reset from external command the drive, I suggest you carefully read the FW manual and in particular the instructions of the parameter group 16.04, where you will find the reset modes indicated both in HW - for example with a digital input - or via fieldbus.
BR
Flavio
Add new comment