I am currently communicating an ac500 plc with another plc via MODBUS TCP / IP (ETH_MOD_MAST) without problems through the Ethernet port, but I need to communicate with a different device via MODBUS RTU Master (COM_MOD_MAST) through the RS-485 port, it is possible to carry out the two modbus communications in parallel taking into account that the connection port you use is different?
Answers
Hi,
Yes, it is possible. Just need to configure correctly COM_MOD_MAST to the corresponding port
Yes, it is possible. Just need to configure correctly COM_MOD_MAST to the corresponding port
Hi,
Yes , you can use COM-1 Communication port and configure it as RS485 and read/Write the data form the controller.
Regards
Mahendra G Patgar
Yes , you can use COM-1 Communication port and configure it as RS485 and read/Write the data form the controller.
Regards
Mahendra G Patgar