How to connect a device with HART protocol to Freelance system (Control Builder F)
Hi,
i want to connect devices with HART protocol to Freelance system, so the question are:
- is it require an aditional equip?
- is it an aditional license required for freelance?
Any additional information is appreciated
i want to connect devices with HART protocol to Freelance system, so the question are:
- is it require an aditional equip?
- is it an aditional license required for freelance?
Any additional information is appreciated
Voted best answer
Hello,
In freelance HART is over profibus, So you need FI 830 (PB Master), CI840 (PB Slave), AI/AO 845 (hart pass through), AI/AO815 (hart pass through), AI/AO 895 ( Intrinsic safe hart pass through) modules where devices get connected and values get pass though hart over profibus.
you can configure this using GSD or via DTM, for DTM you need Professional engineering license, and while installation that feature to be installed.
(If using DTM, you need to install respective HART DTM and ensure compatibility of FDT/DTM's )
It's fairly easy to configure, commissioning and deal with HART or any other communication protocol in Freelance.
Get more details from following manual available in your installation setup.
3BDD012515-111_A_en_Freelance_Engineering_Communication_and_Fieldbusses.pdf
Hope that helps
In freelance HART is over profibus, So you need FI 830 (PB Master), CI840 (PB Slave), AI/AO 845 (hart pass through), AI/AO815 (hart pass through), AI/AO 895 ( Intrinsic safe hart pass through) modules where devices get connected and values get pass though hart over profibus.
you can configure this using GSD or via DTM, for DTM you need Professional engineering license, and while installation that feature to be installed.
(If using DTM, you need to install respective HART DTM and ensure compatibility of FDT/DTM's )
It's fairly easy to configure, commissioning and deal with HART or any other communication protocol in Freelance.
Get more details from following manual available in your installation setup.
3BDD012515-111_A_en_Freelance_Engineering_Communication_and_Fieldbusses.pdf
Hope that helps
Add new comment