No contact with IEC61850 opc server in Service Group
Hi.
The 800xA system was upgraded from 5.1 to 6.0.3.
The IEC61850 project was successfully imported in CET (with update/reload and etc.), put one IED in simulation mode.
But in 800xA in Service Structure/ Event collector/ Service Group IEC61850 shows "no contact with server" error, providers are always in "Synchronizing" state.
Deleted the SG and created again, but no change.
OpcDA_connector SG IEC61850 is even in Error.
What could be the matter?
Answers
This question has not yet been answered.
by Gao Huan Rank: 186 on 3/18/2021 9:38:07 PM | Like (0) | Report
Did you try 3rd party opc client to connect IEC61850 opc server?
by Alexander Rank: 2352 on 3/19/2021 12:48:30 AM | Like (0) | Report
No, but the problem seems to be solved for now.
Put all the IEDs in simulation mode in CET
Add new comment