Panel PP883 - Alarm icon popup
Voted best answer
As long as there are active alarms in the alarm server, the alarm indicator notify window will be displayed, regardless of which screen is active. The color shows the current alarm status, and can be configured for each of the alarm groups. The indicator starts in the upper left corner of the screen in runtime, but can be moved to any position on the monitor in runtime.
The appearance of the alarm indicator depends on the current alarm status. It will show the most severe status of the alarms in the list. The Alarm Indicator disappears when all alarms have been acknowledged, and all alarms have returned to inactive status.
Select General settings in alarm server properties page to decide for which alarm statuses to show the alarm indicator.
Active
The alarm condition is met, and the alarm is not acknowledged
Flashing red
Inactive
The alarm has returned to normal condition, but has not been acknowledged
Flashing green
Acknowledged
The alarm condition is met, and the alarm is acknowledged
Flashing green
Normal
The alarm has returned to normal condition, and has been acknowledged
-

Source: online help