ACS355-03E-15A6-4 fault code A5001
This problem showing when i start the drive and keypad keys where not responding
After on/off the drive for some time also the same problem is coming.
I have 2 unit, if I swapping the panel,shall I change form REM to LOC before removing the Panel??
Thanks .
Answers
Hi
To remove the panel without having a fault from the drive, you must set parameter 30.02 on value 3 - last speed. This way you can remove the panel even if the drive is working remotely. If you are in manual mode, by removing the panel you will no longer be able to shut down the drive. To come to your problem, if the converter signals alarm A 5001 to you, almost certainly or you have a fault in the panel itself, but more likely you have a fault in the communication port of the drive towards the panel. This is a failure that would require the control board to be replaced, and for a drive like yours, it is not cost effective.
BR
Flavio
To remove the panel without having a fault from the drive, you must set parameter 30.02 on value 3 - last speed. This way you can remove the panel even if the drive is working remotely. If you are in manual mode, by removing the panel you will no longer be able to shut down the drive. To come to your problem, if the converter signals alarm A 5001 to you, almost certainly or you have a fault in the panel itself, but more likely you have a fault in the communication port of the drive towards the panel. This is a failure that would require the control board to be replaced, and for a drive like yours, it is not cost effective.
BR
Flavio