ACB ACS880 protection
Hi Dear All
Does anyone know if using ACB is applicable for a 12-pulse ACS880-07 Drive protection? our customer ordered LSGI protections for that.
your helps is appreciated in advance.
Does anyone know if using ACB is applicable for a 12-pulse ACS880-07 Drive protection? our customer ordered LSGI protections for that.
your helps is appreciated in advance.
Voted best answer
Hi
ultra fast fuses are generally recommended to protect the power part of a drive.
If your customer has chosen to use a circuit breaker, it means that someone has verified the feasibility of this choice. If you also tell us the power of the drive, I can check if the manufacturer's protection tables allow it.
BR
Flavio
ultra fast fuses are generally recommended to protect the power part of a drive.
If your customer has chosen to use a circuit breaker, it means that someone has verified the feasibility of this choice. If you also tell us the power of the drive, I can check if the manufacturer's protection tables allow it.
BR
Flavio
Add new comment