ABB PM573-ETH PLC and ABB ACS580 Drive Communiation
HI Experts,
I have an ABB PM573-ETH PLC and an ABB ACS580 Drive. I have to send a new IP address to the Drive. But when I try to do it error comes. it says "THE SUBNET MASK DOES NOT MATCH CONTROLLERS SUBNET" But I have set all the subnet masks to 255.255.255.0. What could be the error?
Thanks in advance,
I have an ABB PM573-ETH PLC and an ABB ACS580 Drive. I have to send a new IP address to the Drive. But when I try to do it error comes. it says "THE SUBNET MASK DOES NOT MATCH CONTROLLERS SUBNET" But I have set all the subnet masks to 255.255.255.0. What could be the error?
Thanks in advance,
Answers
Hi
I must assume, because you have not specified it, that your PLC has a fieldbus communication of the Profinet type for example, that is with CM579-PNIO On the drive side, similarly, you will need to have a Profinet interface, for example a FPNO-21. The IP address of the drive must be programmed inside the drive, in the parameters from group 50 to follow, including the subnet mask. The drive manual can help you with this parameterization
BR
Flavio
I must assume, because you have not specified it, that your PLC has a fieldbus communication of the Profinet type for example, that is with CM579-PNIO On the drive side, similarly, you will need to have a Profinet interface, for example a FPNO-21. The IP address of the drive must be programmed inside the drive, in the parameters from group 50 to follow, including the subnet mask. The drive manual can help you with this parameterization
BR
Flavio