AC800 M OPC server to Matrikon OPC server Communication
Hello All,
I have a 800xA 5.1 version which is running . Now we want to send the data from 800xA to Third Party (Martikon OPC ) OPC server
Kindly send the Procedure
I have a 800xA 5.1 version which is running . Now we want to send the data from 800xA to Third Party (Martikon OPC ) OPC server
Kindly send the Procedure
Answers
Hi!
I wonder why you wan't to aim for this setup?
Is it maybe the Tunneler you are referring to?
An OPC-server is doing what is says; serving clients. Server to server communication seems adding complexity to your system.
There are no problems (except perhaps for DCOM), for the 800xA system to act as a OPC-Server.
To have OPC Data Access directly from 800xA, you can use ANY 800xA node as the OPC-server.
The ProcessId is named "ABB.AfwOpcDASurrogate".
Use a testclient and check!
I would strongly recommend you to consider this solution, redirect your OPC client to a preferable (server) 800xA node and the "built-in" OPC-server.
Regards!
I wonder why you wan't to aim for this setup?
Is it maybe the Tunneler you are referring to?
An OPC-server is doing what is says; serving clients. Server to server communication seems adding complexity to your system.
There are no problems (except perhaps for DCOM), for the 800xA system to act as a OPC-Server.
To have OPC Data Access directly from 800xA, you can use ANY 800xA node as the OPC-server.
The ProcessId is named "ABB.AfwOpcDASurrogate".
Use a testclient and check!
I would strongly recommend you to consider this solution, redirect your OPC client to a preferable (server) 800xA node and the "built-in" OPC-server.
Regards!