Hi
Please have a look on release notes of System 800xA of respective version where the specifications are provided.
Please have a look on release notes of System 800xA of respective version where the specifications are provided.
800xA programming languages comply to IEC61131
IEC 60848 is the Standard for GRAFCET. A programming language extremely similar but not identical to the IEC61131 SFC. The 800xA interpretation of the SFC standard is very good, and substantially better (in my opinion) than Siemens implementation of Grafcet. Even though technically the answer to your question might be "no, its not grafcet", in every meaningful way that answer is practically "yes" - 800xA is compatible.
IEC61499 is a development of 61131 and describes FBD. Yes, 800xA is compliant to 61131 and again the answer is practically "yes" 800xA is compatible.
IEC 60848 is the Standard for GRAFCET. A programming language extremely similar but not identical to the IEC61131 SFC. The 800xA interpretation of the SFC standard is very good, and substantially better (in my opinion) than Siemens implementation of Grafcet. Even though technically the answer to your question might be "no, its not grafcet", in every meaningful way that answer is practically "yes" - 800xA is compatible.
IEC61499 is a development of 61131 and describes FBD. Yes, 800xA is compliant to 61131 and again the answer is practically "yes" 800xA is compatible.