Version Error when commissioning on Freelance Engineering 2019
Voted best answer
Good Morning,
so far you've done everything right.
You now have to check the plausibility of the project.
Select the top entry in the project tree and then activate plausibility analysis.
When the project tree is completely green, select the process station and activate the entire station.
So that your controller works, set the switch on the controller to run, your pictures are still on stop.
Hope that helps.
greetings
T.R.
Answers
A version error means, that what is inside the controller and what Freelance Engineering thinks is inside the controller (application-wise) is different.
After an upgrade of a system, you had to import the CSV file of your project into Freelance Engineering. This process clears everything Freelance Engineering knows about what's inside the controller. Thus a version error is a normal state after an upgrade.
You need to do a plausibility check of the whole project and then do a Load Whole Station for each controller, gateway, and Freelance Operations (in this sequence) in the project.
That'll get rid of the version error.
After an upgrade of a system, you had to import the CSV file of your project into Freelance Engineering. This process clears everything Freelance Engineering knows about what's inside the controller. Thus a version error is a normal state after an upgrade.
You need to do a plausibility check of the whole project and then do a Load Whole Station for each controller, gateway, and Freelance Operations (in this sequence) in the project.
That'll get rid of the version error.
All is ok You just need to do the following
Check the whole program to be sure that it has no error
Then do download whole station for the ps1 controller.
Best regards
Reda
Check the whole program to be sure that it has no error
Then do download whole station for the ps1 controller.
Best regards
Reda
Add new comment