Symphony Plus HC800 Fatal 110(ICI): Module is not responding
Hi
I having a problem with my Backup controller HC800 which is the fault LED is red and LED 1 is red. On the HC800 error code on the manual said NVRAM checksum error and the correction action is to initialize NVRAM. I'm tried to perform hard reset on the HC800 but still failed.
Kindly advise.
I having a problem with my Backup controller HC800 which is the fault LED is red and LED 1 is red. On the HC800 error code on the manual said NVRAM checksum error and the correction action is to initialize NVRAM. I'm tried to perform hard reset on the HC800 but still failed.
Kindly advise.
Voted best answer
Hi,
As previously mentioned, special operation 2 (Initialize and format all NVRAM configuration space HC800) is the first fix for an NVRAM error. Refer to 2VAA001586, ABB Ability™ Symphony® Plus HPC800 SD Series Controller User manual, Section 9.3.
It may pay to check that the battery enable jumper on the side of the module is installed correctly to enable the battery used for the NVRAM. Refer to section 9 of the same manual.
If that doesn't work the module battery may be depleted or you have a faulty module.
BR,
Alan
As previously mentioned, special operation 2 (Initialize and format all NVRAM configuration space HC800) is the first fix for an NVRAM error. Refer to 2VAA001586, ABB Ability™ Symphony® Plus HPC800 SD Series Controller User manual, Section 9.3.
It may pay to check that the battery enable jumper on the side of the module is installed correctly to enable the battery used for the NVRAM. Refer to section 9 of the same manual.
If that doesn't work the module battery may be depleted or you have a faulty module.
BR,
Alan
Source: 2VAA001586, ABB Ability™ Symphony® Plus HPC800 SD Series Controller User manual
Answers
you can try t do "special operation" to NVRAM initialization.
you can find special operation procedure on ABB Ability Symphony Plus HPC800 SD Series Controller User Manual
you
you can find special operation procedure on ABB Ability Symphony Plus HPC800 SD Series Controller User Manual
you
Source: HPC800 User Manual