CP676 Runtime installation fails. AB 2.2.5.663, Panel Builder 600 2.8.1 build 447
Voted best answer
Hi,
1. Usually you don't need to load the runtime independently, it is automatically loaded during download, if it has not been loaded before.
2. There is another option, if nothing else help - Factory Restore -> Format Flash
3. Entering in System Mode, after initial start-up, is a little bit tricky, but it is described in the Panel Builder help:
1. Usually you don't need to load the runtime independently, it is automatically loaded during download, if it has not been loaded before.
2. There is another option, if nothing else help - Factory Restore -> Format Flash
3. Entering in System Mode, after initial start-up, is a little bit tricky, but it is described in the Panel Builder help:
"In System Mode a full interface gives users access to all the tool's options.
A special procedure is required to start the tool in System Mode, or when the standard access procedure cannot be used for some reason. Once activated by this special procedure, the System Settings tool always starts in System Mode.
To access System Mode:
- Execute a tap sequence on the touch screen during the power-up phase. A tap sequence is a high frequency sequence of touch activations executed immediately after the device has been powered.
From the page, restart the panel in Configuration OS mode"
Source: Panel Builder 600 help
by Lyubomir Borisov Rank: 1530 on 1/9/2021 5:50:31 AM | Like (0) | Report