Hello,
In an 800xA SV6. 6.0.3 we are reading historical data trough Information Management ODBC connection.
In some cases, and in some short time period we obtained quality codes not documented in “3BUF001094-600_A_en_System_800xA_Information_Management_6.0_Data_Access_and_Rep
orts.pdf” manual.
I made an inverse engineering and I decodified what the bits mean.
This is the result:
Bit 7 and 8, Good data, decimal 192.
Bit 7, Uncertain data, decimal 64.
Bit 17, Duplicated time stamps.
Bit 18, interpolated.
Bit 19, raw data.
Bit 20, calculated data.
Bit 22, no data.
Bit 23, data lost.
I didn’t can identify the meaning of Bit 25 and Bit 29.
OPC documentation says that bits are defined by de manufacturer and in this case is de ABB AC800 OPC.
Anybody on this forum knows what ABB are representation on those bits?
Next is the table in ABB manual.
The codes who are not documented are, 80040, 1000040, 10040000 and 100400C0.
Regards
Answers
System 800xA has an own set of bits as well (extrapolated by Max Time in Basic History, Time value adjusted [by Trace Knee or Exception Deviation). If I were to guess the 1000xxxx is extrapolation and the xxx4xxxx is adjusted time value (I may be wrong or have mixed up these two).
I believe you can see a translation of some of them you read the points using the Plant Explorer > Log Configuration > Status > Read function. Below Settings, you can set the start time of the read operation and also turn off the status code translation to text to get to see the raw quality codes.