Hi,
I would like to know the process of generating alarms in 800xA for SOE cards with external timestamps. I believe if I use alarm basic condition then the timestamp generated will be of this block and not the DI830. I want time stamping of DI830 in events.
I have gone through the configuration manual but did not found anything relevant which can help.
I would like to know the process of generating alarms in 800xA for SOE cards with external timestamps. I believe if I use alarm basic condition then the timestamp generated will be of this block and not the DI830. I want time stamping of DI830 in events.
I have gone through the configuration manual but did not found anything relevant which can help.
Answers
Please enable the SOE in Card level, use the signal ID in the software module , Enable external time stamp.
Doing software forcing will not generate time stamp events , if you want to test make sure you have the hardware setup and simulate on hardware.
Doing software forcing will not generate time stamp events , if you want to test make sure you have the hardware setup and simulate on hardware.
Didn't you ask the same three weeks ago?
I provided some working samples and references to Online Help in Control Builder M Professional:
https://forum-controlsystems.abb.com/...
I provided some working samples and references to Online Help in Control Builder M Professional:
https://forum-controlsystems.abb.com/...