Automation Builder PM 573 ETH configuration errors
Attached pic shows configuraiton errors for the on the controllers. Program is downloaded but showing errors as shown in attached picture. and is PLC is not going to run mode.
Answers
Hi,
you can check the error code from the Automation Builder help and the solution will be also there
In your attached image Error code is not available so I cant check it from here
wr
you can check the error code from the Automation Builder help and the solution will be also there
In your attached image Error code is not available so I cant check it from here
wr
Hi,
The highest priority error is from class E3 and says some invalid configuration data.
Anyhow, you can set the following:
PM573-ETH Parameters -> Stop on error class = E2
download and go in run state
Then you can investigate where is the wrong configuration.
The highest priority error is from class E3 and says some invalid configuration data.
Anyhow, you can set the following:
PM573-ETH Parameters -> Stop on error class = E2
download and go in run state
Then you can investigate where is the wrong configuration.