We delete two objects from conrol structure and recreate them(FRIQ205,FIRQ0001).after that insert new log configuration aspect in aspect area , but not activate.in addition all of log configuration stored in IM historian.photos related to problem attached;Pls recommend solution for this problem.
Thanks
We delete two objects from conrol structure and recreate them(FRIQ205,FIRQ0001).after that insert new log configuration aspect in aspect area , but not activate.in addition all of log configuration stored in IM historian.photos related to problem attached;Pls recommend solution for this problem.
Thanks
Voted best answer
There are a few things you should check here:
1. Make sure disk quota permit adding more logs (use IM Database Instance Wizard).
2. Make sure Oracle disk space is not 100% filled for any tablespace (use same tool as above).
3. Make sure no corrupted entries remain in log database (use "hsdbmaint -checkDB" and "hsdbmaint -clean" as necessary, both are outlined in the IM Configuration User's Guide).
4. Make sure there are no consistency errors in any Log Template aspect (use the Plant Explorer's Find Tool, search for Aspect Category = Log Template, drop result in Consistency Checker, fix or delete errors).
5. Make sure there are no consistency errors in any Log Configuration aspect (use the Plant Explorer's Find Tool, search for Aspect Category = Log Configuration, drop result in Consistency Checker, fix or delete errors).
6. Make sure all IM services are running OK w/o warning in PASGUI.exe (tool) or IM History Manager (via icon in system tray).
Consider filing a support case with your regional ABB Support Center to obtain professional support.
1. Make sure disk quota permit adding more logs (use IM Database Instance Wizard).
2. Make sure Oracle disk space is not 100% filled for any tablespace (use same tool as above).
3. Make sure no corrupted entries remain in log database (use "hsdbmaint -checkDB" and "hsdbmaint -clean" as necessary, both are outlined in the IM Configuration User's Guide).
4. Make sure there are no consistency errors in any Log Template aspect (use the Plant Explorer's Find Tool, search for Aspect Category = Log Template, drop result in Consistency Checker, fix or delete errors).
5. Make sure there are no consistency errors in any Log Configuration aspect (use the Plant Explorer's Find Tool, search for Aspect Category = Log Configuration, drop result in Consistency Checker, fix or delete errors).
6. Make sure all IM services are running OK w/o warning in PASGUI.exe (tool) or IM History Manager (via icon in system tray).
Consider filing a support case with your regional ABB Support Center to obtain professional support.
Answers
above items are checked and the results are as follow photos.
I performed hsdbmaint -checkDB ,the result is as follow photos.in addition do not see any inconsistency.
I performed consistency check for LC and LT by consistency checker tool and the respective results are as follow photo.so check the errors and warning ,found these are wrong configuration.so delete them.and performed consistency check again and send result photo.
The respective result about hsdbmaint -checkDB are as follow.How do I delete those 28 items?