How to configure signal Tags in 800xA 6.1 IEC61850 connect OPC server
Hi All,
I am working for the first time on the 6.1 version of IEC61850 connect, though I have been working on versions 5.1 -6.0 all the time.
I am not able to find how to configure alarm signals tags (eg. Over Current optd, master trip etc..,), which we used to do in CET in earlier versions.
Has anyone worked on this recently?
Thanks
I am working for the first time on the 6.1 version of IEC61850 connect, though I have been working on versions 5.1 -6.0 all the time.
I am not able to find how to configure alarm signals tags (eg. Over Current optd, master trip etc..,), which we used to do in CET in earlier versions.
Has anyone worked on this recently?
Thanks
Answers
There is a "xxx Event Configuration" Aspect on each Data Object (below the Logical Nodes) where you can configure this. But it should really be done in the Object Type Structure before loading the SCD File... best is you read the Documentation carefully because the workflow is completely changed from older versions...
Process Indication Event to be created in Library Structure\IEC61850 Alarm & Events in 800xA v6.1.
And the same need to be mapped in IED Signal Mapping\Event Definitions against each desired property name before the SCD upload.
And the same need to be mapped in IED Signal Mapping\Event Definitions against each desired property name before the SCD upload.