Hi All, Could anyone help me in understanding the AC800F Diagnostic log file. How to know which task in the program is referred in the task numbers listed in the log file (607/609/611/613/615/617/2945)?? Task Schedule Information ***************************** | Idle Time | Execution Time | Redundancy Time Task | min max avg | min max avg | min max avg ----------------------------------------------------------------------------- 607 | 0 --- 438 | 50 177 56 | 609 | 0 --- 398 | 86 273 102 | 611 | 0 --- 453 | 39 136 46 | 613 | 0 --- 452 | 38 135 48 | 615 | 0 --- 463 | 27 703 36 | 617 | 0 --- 478 | 18 105 22 | 619 | 0 --- 459 | 28 123 41 | 2945 | 0 --- 494 | 5 28 6 | Any technical guide would be really appreciated. Thanks in advance Regards, Sridhar

Voted best answer
You can find the information you need in the project.
Here you have to mark the individual tasks.
You will then see the respective object number via "Show selected objects".
This is referenced in the diagnosis.
Regards
T. R.